#9
Jens


According to Analog Device the ADE7878 has 2 configurations.
-3-Phase, 4-Wire, Wye Distribution Systems : that smartpi is using i think.
-and 3-Phase, 3-Wire, Delta Distribution Systems : this is the system i like to use.
There is a difference of 1,7320 in measurement. The values i measure are to high.
Is it possible to change the software so i can chose for the delta distribution system .
(ACCMODE Register , CONSEL must be set to 01.)


Greetings Luc